    I have kept up with things on our coolong system but it doesnt seem to get the place good and cool.

    Cleaned coils
    keep fresh filters in return.

    Is there something else I should be keeping an eye on?
    WE ARE NOW REALLY TWIN OAKS LANES.

  • #2
    Our cold air return was sucking from above the ceiling tiles up about 18 inches. (90+ degrees when hot) I extended the spout down to the ceiling tile with some siding aluminum coil stock and screws. In the 70's they heated and cooled all of the building, energy was ALOT cheaper then.

    Comment


    • #3
      Start by looking at the temperature drop across the evaporator coil. Measure the temp at the intake side of the coil and then after the coil. Also check the temp at the return air register. It should be about the same as the temp on the intake side of the coil. Also read the temp at the exhaust vent...this temp should be the close to the temp you read on the other side of the evaporator coil.

      Differences in temperatures can let you know if you are getting warmer air from other locations. The drop in temperature across the evaporator should be about 20 degrees or so.

      Post back with temp readings and we can go from there.

      Do you have a set of gauges to see what pressures are in your system?
      TSM & TSM Training Development
      Main Event Entertainment
      480-620-6758 for help or information

      Comment


      • #4
        I dont have those sort of gauges, so I wont be able to check temps and pressures.
        WE ARE NOW REALLY TWIN OAKS LANES.

        Comment


        • #5
          Burn as few lights as needed during the day - light is heat.

          Comment


          • #6
            If you would like to to be cooler...you will need answers. A digital temperature gauge can be as little as $20 from Grainger. Enter digital pocket thermometer into the search bar on Grainger.com and it will give you many choices.

            You can get an inexpensive manifold gauge set to read pressures for about $50 from Harbor Freight. Not a bad investment if you are trying to diagnose your issues.

            The temperature gauge will at least tell you if you have issues with the air stream.
            TSM & TSM Training Development
            Main Event Entertainment
            480-620-6758 for help or information

            Comment

            Adsense Classic 2

            Collapse
             

            Preventative Maintenance - Brunswick All - Bearing Life

            In relation to the recent “B Shaft” failure, I thought I would throw this subject on the table for discussion. I remember when I attended a “Bearing Life” seminar long...
             

            Preventative Maintenance Brunswick A Jets A2 - SC/Dk Pulley Assembly

            Found a bad left needle bearing in the Scissor / Deck Cable Assembly at the Rear Wall House. Needle Bearings are falling out and there is a pile of metal under it. Been 30+...
             

            Preventative Maintenance - Brunswick B-10's Hollar House

            Took a trip back in time to the classic “Hollar House”. The lanes went in in 1908. There was no ABC but according to the current operator, Tom, it became sanctioned when...
             

            Table support assembly

            My night at part job all 32 lanes going of leagues no where to move. Table support assembly broke rod broke # 2 Cell and bent the heck out of wire channel. Changed the Cell,...
             

            Foul Light LED Mod

            Here is a mod I came up with for a foul light unit. I was able to remove the old indicator light bulbs and replace them with ultra bright white LEDs. This should work for about...
            Working...
            X