1. Replaced the safety switch (twice)
2. Replaced the auxiliary switch (3 times)
3. Replaced the entire insides of the power box (5 times)..basically a totally new box 5 times over.
4. Re-wired /replaced wires leading from terminals 2 and 3 in power box all the way to the A&MC box in the back
5. Replaced chassis on both machines (shot in dark)
6. Replaced relay 5 times (see above)
7. Did continuity tests on ALL wires in power box each time I replaced it
8. did continuity tests on in-line fuses and holders.
I think that about covers everything. Here's what is different though. I did a voltage test on terminals 2 and 3 in the power box. I get 24V on terminal 2 but not on terminal 3. I know there is supposed to be 24V on both. I know thats a problem but I dunno where to check after that. Any sure-pik guru's out there with any clue I'd gladly appreciate any input you'd have. Thank you!!!